bigal.nz 61 Posted May 10 Share Posted May 10 Anyone here built a battery box for Lithiums (looking at Victron)? I have seen a design that was stainless, but having a big conductive box must be a bit of a risk - wondered if there is a better material to build it out of? Another person suggested marine ply, but I would be surprised if it meets the fire rating required. Quote Link to post Share on other sites
LBD 186 Posted May 10 Share Posted May 10 2 hours ago, bigal.nz said: Anyone here built a battery box for Lithiums (looking at Victron)? I have seen a design that was stainless, but having a big conductive box must be a bit of a risk - wondered if there is a better material to build it out of? Another person suggested marine ply, but I would be surprised if it meets the fire rating required. If I was having this debate with my-self... I think I would prefer conductive to combustible with possible toxic fumes... exercise caution where cables pass through and ensure that the lid does not contact the terminals if stood on.... Quote Link to post Share on other sites
K4309 405 Posted May 10 Share Posted May 10 If you go stainless, I would line it with a flame proof lining / insulation. The sound proofing foam I've got for my engine is rated as flame proof. I took a blowtorch to it and still couldn't get it to catch. Forget the trade name now, but it was the good stuff from a specialist supplier, not the cheap stuff from Burnsco. About 25mm thick. You can get it without the alloy foil lining, which would be a hassle. Nice and soft cushioning too, which may help to reduce vibration damage to the batteries. Anyway, my point is you can build a good strong stainless box, and reduce the conductive risk by lining it with something both non-conductive and fire-proof. Personally, I'd go for lead carbon batteries instead of Lithium, similar electrical charge / discharge characteristics, fraction of the price and you don't need a circuit board (BMS) to stop them exploding. But you didn't ask that question so I'll keep my thoughts to myself on battery type Quote Link to post Share on other sites
CarpeDiem 531 Posted May 10 Share Posted May 10 4 hours ago, bigal.nz said: Anyone here built a battery box for Lithiums (looking at Victron)? I have seen a design that was stainless, but having a big conductive box must be a bit of a risk - wondered if there is a better material to build it out of? Another person suggested marine ply, but I would be surprised if it meets the fire rating required. Taking into account you said victron and battery, I am assuming you understand that a victron battery is just a box with batteries (cells) inside it.. Why do you want another box? And where will the box be? Understanding why you want a box to put your batteries in to will help with material selection. Quote Link to post Share on other sites
motorb 45 Posted May 10 Share Posted May 10 Honestly, I'm waiting a few more years for the new sodium-ion battery tech to come into the mainstream. It's got all the benefits of lithium with none of the fire hazard, at only a slight weight penalty. It's already on the market so won't take long for victron etc to catch up. In the meantime, I'll stick with my AGM lead acid. Saving 20-30kg isn't going to make much difference for me (and the weight is low down anyway). OK, that wasn't helpful.... stainless is fine for a battery box assuming there's no chafing or shorting, but where is all the heat and gas going to go if it does burn? I'd also consider the situation with thermal insulation of the battery if charge and discharge rates are high and sustained, or conversely if it's too close to a source of high heat or freezing cold. If the worry is loss of the boat and/or a fire on board, I've got to ask if lithium is really the most appropriate choice for anything but the lightest of racing craft. If it's just about managing the additional risk, then the steel box is only one part of your design consideration; location is also very relevant as that fire cannot be put out and will produce a lot of heat and hot toxic gas until it's done. 1 Quote Link to post Share on other sites
Psyche 829 Posted May 10 Share Posted May 10 I doubt that a battery box is going to help much to prevent fire, as the heat has to go somewhere but anyway I went down the rabbit hole of trying to find out what the legislation says with regard to lithium installations. My conclusion is that they really don't want you to know! How about $186 for a copy of the standard https://www.standards.govt.nz/shop/asnzs-3004-22014 Quote Link to post Share on other sites
Zozza 357 Posted May 10 Share Posted May 10 My understanding of all the Lithium style batteries, the Marine LiFePO4 are the least fire hazard of all, perhaps even less of a fire hazard than AGM or old style Lead Acid Golf Cart type. Don't hesitate to put me right though - what I know about electrical things is less than Donald Trump knows about how Tariffs work. 1 1 Quote Link to post Share on other sites
Frank 175 Posted May 10 Share Posted May 10 14 hours ago, CarpeDiem said: Taking into account you said victron and battery, I am assuming you understand that a victron battery is just a box with batteries (cells) inside it.. Why do you want another box? And where will the box be? Understanding why you want a box to put your batteries in to will help with material selection. The outer casing on the Victron Battery in our land yacht is Aluminium ex factory , the electrical inspector considered that to meet the rules without further ado but I built an outer box in ply and lined it with several layers of dry fibreglass from a heat blanket (ex bunnings) . A lithium battery apparently can burn at close to 1000 deg C so aluminium will eventually fail although by that stage you might be in the raft anyway. I think a steel/SS light gauge folded angle frame with some sort of refractory lining or fire proof lining, plenty of options/products out there in blanket or sheet form. . Question is what would you do if the battery caught fire (any battery not just lithium) ? Quote Link to post Share on other sites
bigal.nz 61 Posted May 11 Author Share Posted May 11 Agree with most of what's been said on here. Namely: 1. You ain't putting out a Lithium fire; 2. The battery box venting holes have to be rather big, so its ability to contain is minimal - I think its more about buying time, potentially to evacuate. No better materials suggested so far..... Al Quote Link to post Share on other sites
CarpeDiem 531 Posted May 11 Share Posted May 11 The latest installation standard applies to all batteries - not just Lithium. Stainless Steel is the best option to meet the standard. Battery compartments should be made of non combustible material, they should be corrosion resistant. They should be mechanically or naturally vented to the outside with an air intake from below them that is also from the outside. Structurally sound, well fixed in place. Compartments should be sealed and completely prevent the ingress of fumes into habitual areas. I suggest that you only buy Lithium batteries that are IEC 62619 certified or at the very least batteries with cells that have the same certification. While not currently in the the standard for boats, this is in the current standard for Caravans and Motorhomes, its a matter of when not if this gets to the marine standard. Be aware that not all Victron batteries carry the same level of certification and only a couple of Victron models have the IEC 62619 certification. Lead Carbon and Sodium Ion are just as likely as Lithium Ion to result in disaster if they are not cared for. Quote Link to post Share on other sites
Psyche 829 Posted May 11 Share Posted May 11 Yet for the entire history of yacht batteries in NZ they are in wooden boxes under a bunk with no outside vents fuming away under the squab usually. Number of FLA incidents compared to boating hours is infestiminal. 1 3 Quote Link to post Share on other sites
aardvarkash10 1,114 Posted May 12 Share Posted May 12 17 hours ago, Psyche said: infestiminal In-fes-tim-inal, adj, an infestation of extremely small battery problems. See: extrarodentially and infesterminal 4 Quote Link to post Share on other sites
Island Time 1,297 Posted Thursday at 11:40 PM Share Posted Thursday at 11:40 PM This is what the CURRENT standard Says; 2.9.3 Additional requirements for lithium ion batteries The following additional requirements apply: (a) Lithium ion batteries shall be installed in locations that ensure the battery manufacturer’s specified operating temperature limits cannot be exceeded and are appropriate for the IP rating of the battery and its management system. (b) Each lithium ion battery shall be provided with a battery management safety system (BMS) either integrated into a battery pack or as a separate component located adjacent to the battery. The BMS shall continuously monitor the voltage and temperature of each cell in the battery. (c) All charging sources shall be automatically disconnected by the BMS when voltage exceeds the manufacturer’s recommended maximum. (d) All connected load shall be automatically disconnected by the BMS when the voltage falls below the manufacturer’s recommended minimum. (e) The battery shall be automatically disconnected by the BMS from all connected load and all charging sources when temperature exceeds the manufacturer’s specified maximum. (f) The BMS shall provide an audible and visual alarm at the normal vessel operating position before a disconnection event occurs. (g) Lithium ion battery ventilation air flows shall be in accordance with the manufacturer’s requirements. If specific air flow data is not provided the requirements of Clauses 2.9.2.2 or 2.9.2.3 shall be applied. NOTE: Care must be exercised when disabling charging sources to avoid the risk of elevated voltages that may damage the equipment. Nowhere in the standards do I see a fireproof requirement?? I could have missed something.... OH, and a LiFePo4 battery is EXTREMELY unlikely to catch fire! In fact the ABYC tried to make some catch fire and were unable to. The battery itself is safer than lead acid based, wet, AGM, or VRSLA included. 1 2 Quote Link to post Share on other sites
bigal.nz 61 Posted 16 hours ago Author Share Posted 16 hours ago So where is all this fireproof talk coming from? Quote Link to post Share on other sites
CarpeDiem 531 Posted 15 hours ago Share Posted 15 hours ago The problem is that standard quoted from above isn't the only standard available to us. And the actual complication occurs as there is no legislated installation standard for Li-ion batteries on pleasure craft under 24m in New Zealand. So we end up with organisation's, vendors, forums, electrical inspectors and electricians reaching well intentioned conclusions from the raft of standards and advice available. For instance, when swapping lead acid for Li, Maritime NZ say this: battery cabinets, rooms or enclosures are constructed from a structurally fire-rated, noncombustible material to contain a battery thermal event to allow sufficient time to either evacuate the vessel or, if possible, control the thermal event The government department (Worksafe) which is responsible for the legislation that applies to pleasure craft electrical installations says: The currently cited standard in the Electricity (Safety) Regulations 2010 is AS/NZS 3004.2:2008: Electrical installations—Marinas and recreational boats—Part 2: Recreational boats installations. This is the standard that should be followed. But that standard has nothing to say about Li-ion batteries and furthermore the Regulations only apply if your vessel has a Connectable Installation. 1 Quote Link to post Share on other sites
bigal.nz 61 Posted 14 hours ago Author Share Posted 14 hours ago 40 minutes ago, CarpeDiem said: The problem is that standard quoted from above isn't the only standard available to us. And the actual complication occurs as there is no legislated installation standard for Li-ion batteries on pleasure craft under 24m in New Zealand. So we end up with organisation's, vendors, forums, electrical inspectors and electricians reaching well intentioned conclusions from the raft of standards and advice available. For instance, when swapping lead acid for Li, Maritime NZ say this: battery cabinets, rooms or enclosures are constructed from a structurally fire-rated, noncombustible material to contain a battery thermal event to allow sufficient time to either evacuate the vessel or, if possible, control the thermal event The government department (Worksafe) which is responsible for the legislation that applies to pleasure craft electrical installations says: The currently cited standard in the Electricity (Safety) Regulations 2010 is AS/NZS 3004.2:2008: Electrical installations—Marinas and recreational boats—Part 2: Recreational boats installations. This is the standard that should be followed. But that standard has nothing to say about Li-ion batteries and furthermore the Regulations only apply if your vessel has a Connectable Installation. Which electrical standard is IT quoting from? Quote Link to post Share on other sites
CarpeDiem 531 Posted 14 hours ago Share Posted 14 hours ago 2 minutes ago, bigal.nz said: Which electrical standard is IT quoting from? AS/NZS 3004.2:2014 Quote Link to post Share on other sites
Guest 137 Posted 13 hours ago Share Posted 13 hours ago My diy. (3yrs old) From what I have experienced insurance companies main criteria is that the installation follows manufacturers recommendation and/or is a proprietary system by one of the big manufacturers with a long-standing history, and /or is by the a commercial installer that can prove they have knowledge and history required to combine a multi brand component system. My insurance co had no clue wrt an NZ/Au standard, or ABYC E13 (recommended) for that matter but was adamant that it would only cover me if I could prove I knew what I was doing which was impossible because the weren’t interested in the science only whether I did it commercially and had a track record. All very ad-hoc. So, can’t be the blame game, which is somewhat refreshing as they could have covered me and on an event, say I did it incorrectly and not pay out. MEH, don’t care, as I have confidence in my system and it is way superior to my old FLA. There may be an issue coming up regarding SAE, IEC, or UL testing certifications of cells wrt to diy. And if a standard is ratified , will it be retrospective, as there was no standard covering Lithium 10yrs ago and it was being installed. Quote Link to post Share on other sites
bigal.nz 61 Posted 7 hours ago Author Share Posted 7 hours ago 6 hours ago, CarpeDiem said: AS/NZS 3004.2:2014 So the issue being MNZ want fire proof - the "ANZ" standard doesnt? Quote Link to post Share on other sites
Island Time 1,297 Posted 6 hours ago Share Posted 6 hours ago 1 hour ago, bigal.nz said: So the issue being MNZ want fire proof - the "ANZ" standard doesnt? Yes And standards are NOT normally retrospective. The current NZ legal standard is the one I quoted above. If you are after a commercial vessel install, best to speak with your local MNZ electrical surveyor. Quote Link to post Share on other sites